Default dc power for servers

when are the companies going to start shipping dc power in the servers as a same cost option as ac power. this would be so much bettr as the long term solution for data centers. right now the cost is out of whack.


just think - not having to go through the inversion cycle again on the ups which would save capital and loss on power as well as not having to run tranformers everywhere in the dc for ac .

finally - no more harmonics - woot!
__________________
www.atlantanap.com premier carrier neutral colocation
netdepot.com premier unmanaged servers
tranxactglobal.com amazing managed and unmetered servers
gnax.net route optimized bandwidth AS3595 since 1994
Reply With Quote
  #2  
Old 11-29-2007, 04:37 PM
cernst cernst is offline
Member
 
Join Date: Feb 2007
Posts: 70
Default

wouldn't you have large power loss just in delivering the power to the equpment due to resistance in the cable?

Power comes from the utility company as AC. In one way or another, it still gets converted from AC to DC. What would the benifits be to converting on a data center scale versus server scale. The only benifit would be one standard power factor/PSU efficiencty for all equipment...which could be good or bad depending on the AC PSU that comes with the equipment.
__________________
YRCW Technologies
Kansas City
Reply With Quote
  #3  
Old 11-30-2007, 02:37 AM
sailor sailor is offline
Junior Member
 
Join Date: Oct 2007
Location: atlanta
Posts: 20
Send a message via AIM to sailor
Default

Quote:
Originally Posted by cernst View Post
wouldn't you have large power loss just in delivering the power to the equpment due to resistance in the cable?

Power comes from the utility company as AC. In one way or another, it still gets converted from AC to DC. What would the benifits be to converting on a data center scale versus server scale. The only benifit would be one standard power factor/PSU efficiencty for all equipment...which could be good or bad depending on the AC PSU that comes with the equipment.
well couplf of huge reasons

in a ups system you convert the ac to dc and then back to ac to deliver to the servers.

an ac inverter (power supply in the computer) produces harmonics.

wouldnt it be good to eliminate that out of the deal and eliminate a conversion step out of the deal as well so you have less equipment and less loss.

you would not have much more loss on the short runs of dc as 48 volts vs the 120 volts anyway compared to the losses in a ups and the transformers.
__________________
www.atlantanap.com premier carrier neutral colocation
netdepot.com premier unmanaged servers
tranxactglobal.com amazing managed and unmetered servers
gnax.net route optimized bandwidth AS3595 since 1994
Reply With Quote
  #4  
Old 12-13-2007, 01:35 AM
Zitibake Zitibake is offline
Senior Member
 
Join Date: Dec 2005
Posts: 113
Default

Quote:
Originally Posted by sailor View Post
well couplf of huge reasons

in a ups system you convert the ac to dc and then back to ac to deliver to the servers.

an ac inverter (power supply in the computer) produces harmonics.

wouldnt it be good to eliminate that out of the deal and eliminate a conversion step out of the deal as well so you have less equipment and less loss.

you would not have much more loss on the short runs of dc as 48 volts vs the 120 volts anyway compared to the losses in a ups and the transformers.
UPSes store power using DC, but typically using 480 volts. Somehow, you're going to have to step that down to 3.3v or 5v at the server, and I doubt doing a DC 480v->DC 5v conversion is really any more efficient than AC 480v -> DC 5v.

Infrastructure costs and power losses can be reduced by keeping power at the highest voltage practical, as close to the equipment as possible. For example, if bladeserver and SAN manufacturers started using 277v NEMA L7 plugs, that would be very convenient: no PDU would be needed; just run 480v 3ph to the RPPs, with one breaker pole per circuit (and likely just one circuit per cabinet, if 277v x 30A). The UK is already doing this with their 230v phase-to-neutral power for servers, which saves them a couple percent in energy efficiency over US 208v.

You would still want to minimize the number of power supplies converting hundreds of volts down to 3.3, 5 or 12 volts DC. That could mean using a very large bladeserver chassis, holding dozens of cards, with just a few large power supplies powering the whole chassis. Running 5v DC is easier over a hard backplane than over flexible cables. A 42U-high bladeserver chassis might even look like a cabinet (no external cabinet needed).

...oh, wait, maybe I'm just thinking of the IBM "Blue Gene" .
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 04:13 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.