Default hot air outlet

it's basic physics that hot air is light and it rises up and the cool air being dense, settles at the base. and it is also efficient practice not to let the two mix in a data center. what i dont get is since the hot air is already rising up, why cant we provide outlets near the ceiling so that the air does not mix? why do we need complicated designs to accomplish this?
Reply With Quote
  #2  
Old 12-23-2011, 04:16 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Good thinking. Actually, it's quite common to use the space above a dropped ceiling as a return air plenum. Installing actual ductwork is quite a bit more complicated and expensive.


Ken
__________________
DR/BC Planner
Reply With Quote
  #3  
Old 12-24-2011, 10:08 AM
honeyclarck honeyclarck is offline
Junior Member
 
Join Date: Dec 2011
Posts: 6
Default

I am new in this field and i not understand your question what you said? Plz tell me more about your question.
Reply With Quote
  #4  
Old 12-27-2011, 12:17 PM
bell bell is offline
Member
 
Join Date: Dec 2011
Posts: 77
Default

@ Ken, are you saying that it is quite possible to just provide just an opening in the ceiling near the hot aisle and expect efficient cooling to take place? or is it necessary to feed the hot air back to CRAC?
Reply With Quote
  #5  
Old 12-27-2011, 12:24 PM
bell bell is offline
Member
 
Join Date: Dec 2011
Posts: 77
Default

hello honeyclarck,

i mean that in data centers, a lot of power is being consumed to ensure proper cooling. In order to reduce power consumption, a common practice is to keep the cold air and the hot air from mixing. for that a lot of spe############ts develop expensive strategies. my question is why we cant just let the hot air that is anyway rising to the ceiling escape from a small outlet instead of all the complicated designs.
Reply With Quote
  #6  
Old 12-27-2011, 03:48 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Quote:
Originally Posted by bell View Post
@ Ken, are you saying that it is quite possible to just provide just an opening in the ceiling near the hot aisle and expect efficient cooling to take place? or is it necessary to feed the hot air back to CRAC?
Top-fed CRACs are usually equipped with collars to connect them to the ceiling plenum. Return air grilles can be strategically placed above the hot aisles to maximize hot air return. Sometimes the racks are also ducted directly to the ceiling.

Ken
__________________
DR/BC Planner
Reply With Quote
  #7  
Old 12-29-2011, 06:16 AM
sweetgreen sweetgreen is offline
Banned
 
Join Date: Dec 2011
Posts: 61
Default

can the heat obtained from the hot aisles be utilized to produce small scale electricity?
it seems like a shame to let all that heat go waste..
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 01:06 AM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.