Default Question regarding access to aisles

I have a customer who has inquired about the requirement of having a walkway between a set of racks to allow a person to easily get from row to row. They currently have a 36" clearance between 2 of the racks that allows them to pass through. I am not too sure if there are any code compliance issues with sealing off that pass-through with more cabinets. The concept appears to conflict with establishing hot-aisle cold aisles.

Here is the layout:

We have an aisle that is 9 cabinets deep. The aisle next to it also laid out to allow 9 cabinets deep. However, currently there is 7 cabinets deep, with a 36" pass-through, with the 9th rack already in place.

The issue would be an non-issue in a scenario where cabinets are in the middle of the room, from what I understand. However, the 9th racks are butted against an exterior wall.

Is the 36" gap required for access in to that row? I know it is a nice thing to do for personnel, however, not ideal for allocating space for racks in a full datacenter.

An additional note: the area between the 2 aisles is 3ft wide and serves as a hot aisle...

Please let me know your thoughts.

Regards,
Keith
Reply With Quote
  #2  
Old 08-08-2006, 04:38 PM
Rmgill Rmgill is offline
Moderator
 
Join Date: Jun 2006
Location: Atlanta, Ga
Posts: 28
Default

I'd check with code to be sure. There are requirements for either depth of the aisle OR a second exit. This is to prevent someone being trapped if there is a fire or electrical fault. Not as big a deal in a rack of computers, but codes enforcement officers are often quite strict about such things.
__________________
CNN Internet Technologies
Data Center Manager
Reply With Quote
  #3  
Old 08-15-2006, 01:46 PM
Keith's Avatar
Keith Keith is offline
Administrator
 
Join Date: Aug 2006
Location: Washington DC Metro Area
Posts: 225
Send a message via AIM to Keith Send a message via MSN to Keith
Default

Thanks for the response Rmgill and I appologize for the delayed follow-up. I just received a call back from the fire marshal in our area and he indicated that as long as we have 36" clearance between the racks, we will not require a second exit.

Gotta love code jurisdictions ;-)
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 10:41 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.