Default Why an 80% cushion?

Hello all
New to this forum and kind of new to data centers. My question is why do we not go above 80% of a power strips rating and would it be okay to ocassionaly go over that 80% limit without surpassing the total breaker rating.

Thanks in advance for your time.

Nick
Reply With Quote
  #2  
Old 05-25-2011, 02:45 PM
kdebs kdebs is offline
Junior Member
 
Join Date: Mar 2011
Location: Detroit, MI
Posts: 12
Default

That 80% is mandated in the USA by the National Electrical Code. For continuous use (3 hours or more, i.e. servers that are always on inside a data center), circuit breakers are rated at 80% of their nominal capacity. It's okay to go above 80% use, but it's not okay to stay there.
__________________
Colocation & data center services in Detroit Michigan.
Reply With Quote
  #3  
Old 06-04-2011, 11:54 AM
emad emad is offline
Member
 
Join Date: Jan 2011
Posts: 61
Lightbulb

So do you think it is only for US datacenters?
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 10:36 AM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.