Default Precision Aircon + Comfort Type AC as Backup

Hi,
I am tasked to make a research for the best and most practical approach in replacing our old sets of Precision Aircon Unit (PACU) being used for our Data Center. Since cost is a factor, below are the options being considered:
OPTION 1: To purchase 3 units of PACU @ XX TR each plus 1 unit of Comfort Type (CT) as their backup - The idea is whenever one PACU need to be temporarily shutdown for a certain reason (i.e., preventive maintenance, unit failure, etc.,) the CT will be used as an additional AC. Thus, 2 units of PACU and 1 unit of CT will be operational for the time being. Once the PACU being maintained becomes operational again, the CT will be shutdown to operate all PACUs again.

OPTION2: To purchase 1 unit of PACU @ XX TR plus XX units of CTs as its backup - The idea is almost the same as OPTION 1, i.e., whenever the PACU needs to be temporarily shutdown for a certain reason (i.e., preventive maintenance, unit failure, etc.,) the CTs will be used as temporary cooling solution. Once the PACU being maintained becomes operational again, the CT will be shutdown to operate using PACU again.


Question: Are both options advisable? If yes, which is better? Or using CT as a backup AC for PACU is really not a "good" idea? Your inputs are highly appreciated.

Thanks,
Joel
Reply With Quote
  #2  
Old 08-17-2006, 12:22 AM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

I'd use multiple precision air units for computer room cooling in an N+1 architecture. This allows for planned or unplanned outage of one unit while the remaining ones carry the load. In your case, make sure the electrical load never exceeds the capacity of 3 units. Why would you use a comfort unit?
Reply With Quote
  #3  
Old 08-17-2006, 01:07 AM
joelcching
Guest
 
Posts: n/a
Default

Hi KenB,
Thanks a lot for your reply!
Regarding why would we use a comfort type is mainly because we would like to explore the practical side of it (since cost is a factor). Comfort Type is a lot cheaper than the PACU, we are thinking of using them just for short term use, i.e., in case our PACU is under maintenance. Although we have not decided this yet. We are still at the planning and research stage. Our objective is to have the right solution so that our investment will be worth it.


Regards,
Joel

Last edited by joelcching; 08-17-2006 at 05:05 AM.
Reply With Quote
  #4  
Old 08-23-2006, 02:49 PM
Rmgill Rmgill is offline
Moderator
 
Join Date: Jun 2006
Location: Atlanta, Ga
Posts: 28
Default

If a CT unit is shut down and not run for some time how do you know it's still operational when you need it? Are you thinking Chilled Water or Something else?
__________________
CNN Internet Technologies
Data Center Manager
Reply With Quote
  #5  
Old 08-25-2006, 04:52 AM
joelcching
Guest
 
Posts: n/a
Default

Hi,
We are thinking of a split type floorstander AC. Thanks!
Reply With Quote
  #6  
Old 09-04-2006, 01:33 AM
Keith's Avatar
Keith Keith is offline
Administrator
 
Join Date: Aug 2006
Location: Washington DC Metro Area
Posts: 225
Send a message via AIM to Keith Send a message via MSN to Keith
Default

Relocating thread to the Datacenter Development forum.

Please feel free to post replies to this thread from within the datacenter development forum.

--Keith
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 05:24 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.