Default Trace power

Our PowerWare UPS shows output levels across 3 phases. They are listed as phase A,B, and C. Phase C is currently at 75% while phase A&B are below 30%. Some of the outlets in the floor are labeled A, B, or C and some are not. I tried moving some equipment to an outlet labeled phase A from a outlet labeled phase C but that seemed to increase the load on phase B; This lead me to believe some of the outlets are mis-labeled.

I can call in an electrician to trace everything but it seems like there should be an easy way to trace them myself. I thought about plugging in some type of resister and watching the graph on the UPS but I could not find any simple off the shelf tool out there.
Reply With Quote
  #2  
Old 08-06-2008, 12:03 AM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

zmanea,
Hi, and welcome to the forums! Check out this thread: http://www.datacentertalk.com/showth...ghlight=tracer


Ken
Reply With Quote
  #3  
Old 08-06-2008, 02:56 AM
zmanea zmanea is offline
Junior Member
 
Join Date: Aug 2008
Posts: 4
Default

Thanks for the reply KenB. The power comes out of the UPS into a junction box and then breaks off into multiple outlets in the room. The junction box has 4 sides with multiple circuits coming out of each side. Each outlet is properly labeled to where it connects on the junction box but there is no information regarding what phase each one is.
Reply With Quote
  #4  
Old 08-06-2008, 04:16 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

A high-current single phase device, such as a space heater, should make a noticeable change in one of the UPS meters. Remember that circuits with two hots (such as 208V in the US) will use a pair of phases.

Ken
Reply With Quote
  #5  
Old 08-07-2008, 02:05 AM
zmanea zmanea is offline
Junior Member
 
Join Date: Aug 2008
Posts: 4
Default

That actually worked perfectly! It definitely confused a couple of coworkers but it got the job done.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 05:19 AM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.