Default datacenter generator testing

Hi, I'm new to the forum and hoping I will be able to give and receive valuable information . I have a question on what the industry standards are for datacenter diesel generator testing. I am wondering how often it should be started and how often for a full load test. I believe we do an annual simulated load test with a load bank and then start generator every 2 weeks and run for 5 minutes. This does not seem sufficient to me and I'm wondering if anyone has a link showing best practice and industry standard that I can use to support my theory. thanks Steve
Reply With Quote
  #2  
Old 06-10-2005, 01:19 AM
SiteSouth SiteSouth is offline
Senior Member
 
Join Date: Oct 2004
Location: Atlanta, GA
Posts: 132
Send a message via AIM to SiteSouth
Default

That seems about normal. The only thing I would change is doing the load test each quarter.
__________________
http://www.global-enterprise.com -
- colocation and dedicated servers -

Atlanta, GA and Las Vegas, NV
Reply With Quote
  #3  
Old 06-11-2005, 02:35 PM
kjbaudry
Guest
 
Posts: n/a
Default

We work with a number of companies and everyone has their own policy and reasons (or in some cases lack of reasons for it). How you do it takes knowledge of standards but is mostly about using common sence (the least common of the sences) and good judgement.

Things to consider:

I believe that NFPA requires life-safety generators to be exercised every two weeks for 20 minutes, under load. This has been a long standing requirementy and I assume has some research behind it. However, its not applicable to a data center and a failure during testing only causes an inconvenience.

My belief is that a generator should be normally tested weekly without load, with at least one week per month under building load. Finally once a year with a full load bank test.

The monthly test under building load should be by opening the main, NOT by exercising the generator from a remote start/transfer control button.

My reasoning is that the ATS needs to be exercised regularly and including your voltage sensing relays and controls.



Could my PM/Testing cause a failure? Probably not, but it could cause a pending failure to show itself at the time of the test rather then when power fails and the generator is required. Some people believe that it's better to wait until the failure occurs rather then instigate a failure. This line of reasoning is naive and fear based. Consider that during testing you have the ability to switch back to untility power. Providing that your UPS should carry your critical load and you can retart the HVAC in a timely manner.

When should we test? If you test during normal business hours you run the risk of causing an outage during prime time. This is true but on the other hand, you likley have staff and other resources available to get you back up and running.

Precautions:
1.
Reply With Quote
  #4  
Old 06-11-2005, 02:43 PM
kjbaudry
Guest
 
Posts: n/a
Default

We work with a number of companies and everyone has their own policy and reasons (or in some cases lack of reasons for it). How you do it takes knowledge of standards but is mostly about using common sence (the least common of the sences) and good judgement.

Things to consider:

I believe that NFPA requires life-safety generators to be exercised every two weeks for 20 minutes, under load. This has been a long standing requirement and I assume has some research behind it. However, its not applicable to a data center as a failure during testing only causes an inconvenience.

My belief is that a generator should be normally tested weekly without load, with at least one week per month under building load. Finally once a year with a full load bank test.

The monthly test under building load should be by opening the main, NOT by exercising the generator from a remote start/transfer control button.

My reasoning is that the ATS needs to be exercised regularly and including your voltage sensing relays and controls.

I've seen too many failures because of not transferiing to building load under consditions that mimic real life.

Could my PM/Testing cause a failure? Probably not, but it could cause a pending failure to show itself at the time of the test rather then when power fails and the generator is required. Some people believe that it's better to wait until the failure occurs rather then instigate a failure. This line of reasoning is naive and fear based. Consider that during testing you have the ability to switch back to untility power. Providing that your UPS should carry your critical load and you can retart the HVAC in a timely manner.

When should we test? If you test during normal business hours you run the risk of causing an outage during prime time. This is true but on the other hand, you likley have staff and other resources available to get you back up and running.

Precautions:
1. All interested parties should be notfiied of when the testing will be performed.
2. Testing schedule should be coordinated with key activities such as data backup, quartery accounting runs, etc.
3. You should have a checklist to run through before you run your generator test (verify that UPS is normal, HVAC chillers & AHUS are running, etc.
4. If you don't have a battery monitor on your UPS system you should check for ripple current with a hand held ammeter (especially if your using VRLA batteries and don't have multiple strings).
4. Arrange your testing such that HVAC is serviced the day before the generator tests.
5. Arrange to have the appropriate service personnel on site or clsoe at hand.
6. After the test you should walk through and check taht all is well.

When you test without load you just need to run the genset long enough to coem to full temperature and allow the retransfer relay to shut it down. When testing under building load 20 minutes is probably more apprpriate. For the annual load bank test, a lot of people want 8 hours but I prefer either two or four hours. Two hours is sufficient to undcover any problems.

If you have redundant generators then you should rotate allowing the pair to carry the load and then one with minimal load sharing then the other.

Ken Baudry
www.kjbaudry.com

Last edited by kjbaudry; 06-11-2005 at 02:49 PM.
Reply With Quote
  #5  
Old 09-19-2014, 05:36 PM
Ynasnnetwe Ynasnnetwe is offline
Junior Member
 
Join Date: Sep 2014
Posts: 17
Default

Thank you for##good##communication.
Reply With Quote
  #6  
Old 10-15-2014, 12:33 PM
Ynasnnetwe Ynasnnetwe is offline
Junior Member
 
Join Date: Sep 2014
Posts: 17
Default

Thank you for##good##communication.
__________________
dubli
Reply With Quote
  #7  
Old 06-22-2016, 11:15 AM
adilkhan009 adilkhan009 is offline
Senior Member
 
Join Date: Feb 2016
Location: Mumbai
Posts: 1,084
Default

Testing generators and inspecting batteries are just part of maintaining a backup power system that can help prevent unexpected data center downtime.
Reply With Quote
  #8  
Old 11-27-2016, 01:37 PM
next434 next434 is offline
Junior Member
 
Join Date: Nov 2016
Posts: 20
Default

Hello! I am also a beginner, but I run the generator every 2 weeks. I think it is correct)
Reply With Quote
  #9  
Old 01-01-2017, 10:59 PM
next434 next434 is offline
Junior Member
 
Join Date: Nov 2016
Posts: 20
Default

Hello! I am also a beginner, but I run the generator every 2 weeks. I think it is correct)
__________________
wwwcomcast.net
Reply With Quote
  #10  
Old 01-31-2017, 11:40 PM
riyanamoss riyanamoss is offline
Junior Member
 
Join Date: Jan 2017
Posts: 2
Default

Hello, I am totally agreed with the kjbaudry's explanation here. All the points are good and enough to explain your question's answer here.

_____
web application security testing tools
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 07:45 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2021, vBulletin Solutions, Inc.