Go Back   Data Center, Colocation, Cloud Computing, Storage, Dedicated Servers Forums > General DataCenter Discussion Forum > Data center general discussion and solution

Reply

 

Thread Tools
  #1  
Old 07-20-2009, 12:19 PM
smilers smilers is offline
Junior Member
 
Join Date: Jul 2009
Posts: 10
Default Power to DC

Hi Guys,

I seek your help,i been posted to facilties support and been reading abt DC operations lately. Please let me know if the picture of power being transmitted is correct.

Power from Substation in KV (e.g. 22KV)

To the buiding with DC, it will first go to the transformer and step down to V(e.g. 415 V) then to another transformer step down again to 230 V

Then splits to UPS & Generator where it is measured in KVA (e.g. 100KVA)

and goes to DC and servers in KW.

PLS correct me if im wrong

Now, what is the power of 230V in laymen terms..is 230V going into each DC or is 230V being shared by 5 DC or 230 V for a whole 10th storey office buidling?

How much power comes in to a office building generally?

How does it work? Pls help..
Reply With Quote
  #2  
Old 07-20-2009, 01:27 PM
Schumie Schumie is offline
Senior Member
 
Join Date: Dec 2008
Location: Thatcham, UK
Posts: 160
Send a message via MSN to Schumie
Default

I'd recommend that you speak to an building electrical design engineer - this is not stuff to play around with and mistakes are generally very costly (both financially, and in human life).
Reply With Quote
  #3  
Old 07-29-2009, 09:35 PM
jamesb jamesb is offline
Member
 
Join Date: Feb 2009
Posts: 28
Default

I would have to agree with Schumie on this one. Unless you are 100% certain about what you are doing I would recommend for you to talk to a spe############t.
Reply With Quote
  #4  
Old 08-25-2009, 04:17 AM
smilers smilers is offline
Junior Member
 
Join Date: Jul 2009
Posts: 10
Default

Thanks for your feedback guys...
Reply With Quote
  #5  
Old 08-27-2009, 08:49 PM
sirplank sirplank is offline
Junior Member
 
Join Date: Mar 2009
Location: Sweden
Posts: 5
Default

Hi smilers,

Your picture is almost right.

I presume you are not the designer for the data center, at least not for the electricity, but only wants to understand the basics.

You receive power from a power station where voltage may differ from 11kV to 220kV, this can probably be other values in different countries.

After this you want to transform it into 400V and keep it there for distribution.

Distribution starts with a switchgear where you manage connections to possible backup generators and UPS including batteries.

After the UPS you go back to the switchgear and put up fuses for distribution to all zones. For example our data center we use 400A for both A- and B-system for each row of racks.

At each end of a row of racks a distribution board is put up with fuses for each rack. A note is that we're still on 400V.

To provide the customer with desired voltage you split your three-phase 400V into one-phase 230V. This is done without a transformer. I'm not that into electricity and english language to explain the procedure for how this happens but you'll get the picture.

Hope this helps.

Also understand that this is how I built our data center. It can be done in numerous other ways, for example consider your customers only use 48V direct current rather then 230V actual current. This will be another scenario.

Regards,
Mike
Reply With Quote
  #6  
Old 08-30-2009, 10:40 AM
embryo embryo is offline
Junior Member
 
Join Date: Jul 2009
Posts: 1
Default

I think siplank has a good point. I think its better to listen to him to aviod any problems later.
Reply With Quote
  #7  
Old 09-02-2009, 02:07 AM
smilers smilers is offline
Junior Member
 
Join Date: Jul 2009
Posts: 10
Default

Its much clearer now..

Thanks Mike
Reply With Quote
  #8  
Old 09-25-2009, 04:50 AM
lovely09 lovely09 is offline
Junior Member
 
Join Date: Sep 2009
Location: Birmingham,UK
Posts: 13
Default

Mike has a good point with all those computation fro electricity and other things.I'm not a professional with this matter and i agree to Schumie,an electrical design engineer will answer more of your question specifically when you apply it in actual basis.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 07:23 AM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.