Default UPS question

We are running around 30 servers on 42U rack. If I want to run UPS for least one to 2 hours, what are the factors I need to consider such as brand name, power out put, etc.

Thanks
Reply With Quote
  #2  
Old 10-02-2008, 04:32 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Tom,
I would say you should select the UPS based on the following:

- Capacity - Based on electrical demand of equipment you want to power, now and in the future
- Batteries - Based on how long you want equipment to run without utility power -- more batteries, longer runtime
- Topology - Online or offline, depending on your need for reliability and continuous power conditioning
- Configuration - Based on the number and types of outlets and voltage your equipment needs
- Communications - Based on need to shutdown host equipment automatically in case of power outage and/or monitor UPS status via network
- Form factor - Based on need for rackmount ability
- Cost - Your budget (check shipping costs)
- Manufacturer - Popular US brands are APC, MGE, Emerson/Liebert and Powerware

Keep in mind that without cooling, most equipment will overheat sooner or later, so let that guide your runtime goal. Here is a pretty good layman's guide to UPSes: Information about power UPS , Uninterruptible Power Supplies and Power Protection

Hope that helps.

Ken

Last edited by KenB; 10-02-2008 at 06:17 PM.
Reply With Quote
  #3  
Old 10-02-2008, 06:10 PM
tom tom is offline
Member
 
Join Date: Sep 2008
Posts: 58
Default

Ken,

Thanks a lot for your help.
Reply With Quote
  #4  
Old 10-03-2008, 01:13 PM
HHSS HHSS is offline
Junior Member
 
Join Date: Aug 2008
Location: Århus, Denmark
Posts: 17
Send a message via ICQ to HHSS
Default

In addition the above mentioned, I would reccomend not to forget your TCO. Check the effeciency on the UPS, the installation costs and also the following service costs.
In order to get the most out of your batteries, the room temperature should be static around 20 Celcius (depending on the manufactor), so perhaps if possible, it would be a good idea to have the UPS in a seperate room than where your HW is.
Some UPS brands such as MGE allows the opertunity to upgrade the UPS by exchanging the power module and the isolation transformer. This means, that in case you infrastructure grows, you don't necesarrily need to purchase a new UPS, but you can just upgrade the existing one.
BTW - don't forget to consider redundancy.
__________________
Henrik Svendsen

Datacenter System Architect
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 11:56 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.