Default Power calculation for server racks

Hi Folks,

Need some light on power calculation in Data Centre.

Server rack has 2 power source A & B.

3 KW power is catered to this rack.

And assuming readings at Rack show 3 KW for both powerstrips.

Does is mean this rack can use 3 kw from A source and 3 KW from B source? If so, then this rack is using 6 KW?

If i conclude rack is drawing only 3KW although it has source A & B. Then, incoming power at DB or UPS would show 3 KW for each UPS.
ie. UPS A = 3 KW
UPS B = 3 KW

Both UPS = 6 KW

Please enlighten. Thanks.
Reply With Quote
  #2  
Old 06-03-2012, 05:06 AM
Neoeclectic Neoeclectic is offline
Member
 
Join Date: Oct 2008
Posts: 85
Default

The standard rules are 50% and 80%.

50% if you want absolute redundancy. 80% is the maximum allowed load according to USA electrical code standards. I'm not sure what the codes are for other countries. But never should it be 100%. If you have 6kW total to a cabinet 2.4 kW per power strip is what you should be aiming for in actual usage.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 04:42 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.