Default Rack and isle size?

Whats the optimum rack depth for a new data centre? 1000mm or 1200mm?

Also, what isle width is considered "good practice" in a hot/cold isle system with under floor cooling?

Thoughts please gentlemen/ladies...
Reply With Quote
  #2  
Old 03-13-2008, 01:45 AM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Hi, Cougar. Welcome to the forums. The answers really depend on what type of equipment you expect to deploy. We just finished remodeling a small, traditionally (subfloor) cooled, general purpose data center. Today we're mostly using 1U and 2U servers and disk arrays, but we anticipate more blades and other higher density form factors sooner or later. Here's what I think:
  • Rack Depth: 1200 mm (48") - Allows increased equipment depth and in-rack cabling space
  • Cold Aisle Width: 1800 mm (72") - Increases air supply by 50% vs. 1200 mm aisles
  • Hot Aisle Width: 1200 mm - Provides adequate rear rack service area, aligns racks with floor grid to optimize subfloor access
Overall, since anticipating the future is an inexact science, expect to be wrong on some dimension -- space, power, cooling, cableway, floor loading, etc. Be sure to have a plan for 1) providing more of that resource when you run out, or 2) how to avoid running out.

I hope others will chime in with their views.


Ken
Reply With Quote
  #3  
Old 03-13-2008, 07:25 AM
Cougar Networks Cougar Networks is offline
Junior Member
 
Join Date: Mar 2008
Location: Kent
Posts: 2
Default

Thanks Ken. Very valuable info.

Matt..
Reply With Quote
  #4  
Old 03-13-2008, 02:09 PM
cernst cernst is offline
Member
 
Join Date: Feb 2007
Posts: 70
Default

Hot / Cold aisles are a must.

A standard rack depth for traditional servers is 40 - 42 inches. If I were you, leave off the cable management arms...but do have cable management system in the rack!
I am just implementing blade racks and I will not use anything less than 48 inches. Unfortunately our networking team is dictating the use of pass-through network blades on the chassis so they can sniff individual servers...so I can have the potential of 102 copper cables in a rack with just 3 blade chassis....136 with 4 chassis...and then there are fiber storage lines....and power cables.

I've heard that two tiles should be your cold aisle and one tile should be your hot aisle. There are always pros and cons. Your cooling capacitiy and cooling distribution needs to be considered. Opening up a third row of tiles may allow too much air flow and create hot spots may occur in other sides of the data center (I've done that).
__________________
YRCW Technologies
Kansas City
Reply With Quote
  #5  
Old 03-13-2008, 04:14 PM
dcrelocation dcrelocation is offline
Member
 
Join Date: Feb 2008
Posts: 38
Default

Aisle space is important, but there's no standard measurement because the space between aisles depends on the racks and cooling system you've employed. Ideally, to aid in cooling, you'll space racks at least four feet apart, increasing to six to 12 feet apart when power consumption exceeds 5 kW per rack. But this may be impractical in high-density environments. Hot/cold aisle configurations, implemented with CRAC units, let racks be placed closer together. Depending on your High Density cooling strategy will also add to the distance between the racks and ceiling heights. If you have low ceilings you may want to have a larger hot aisle as well.
Reply With Quote
  #6  
Old 03-14-2008, 12:10 AM
SuperRacks SuperRacks is offline
Member
 
Join Date: Feb 2005
Location: NL- Rotterdam
Posts: 64
Send a message via ICQ to SuperRacks Send a message via AIM to SuperRacks Send a message via MSN to SuperRacks Send a message via Yahoo to SuperRacks
Default

Remember that the wider the corridors are, the less footprints you will be able to put in place. So less ROI as far as space is concerned.

Lock the cold corridor down as much as you can (place doors and roofs), more than 100cm rack depth is -in my opinion- a waste of space and air pressure. Keep the pressure under (the floor) as high as you can and put blinds in every unused unit.

Furthermore, let customers pay for used power instead of default power use (lets them buy low voltage units).
__________________
European hosting at toplevel !
Reply With Quote
  #7  
Old 03-18-2008, 06:45 PM
dcrelocation dcrelocation is offline
Member
 
Join Date: Feb 2008
Posts: 38
Default

Here is a link of a white paper APC wrote. I do not agree but this may help.

http://www.apcmedia.com/salestools/V...YMZ7_R0_EN.pdf
Reply With Quote
  #8  
Old 03-20-2008, 03:50 AM
Zitibake Zitibake is offline
Senior Member
 
Join Date: Dec 2005
Posts: 113
Default

Quote:
Originally Posted by dcrelocation View Post
But this may be impractical in high-density environments.
Anyone have suggestions for hot or cold aisle width if you intend to use in-row or overhead cooling?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 12:31 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.