Default Infrared Thermometer for Data Center HVAC measurements

Looking for a Infrared Thermometer for Data Center HVAC measurements. Is the Fluke 561 too overdoing it or Fluke 62 Mini sufficient? Any recommendations?

Some good recommending tools available, but would like to hear some experiences from the field.

http://us.fluke.com/fluke/usen/produ...tureSelect.htm

http://tools.fluke.com/SpotSize/spotsize.aspx

Ed
Reply With Quote
  #2  
Old 05-26-2010, 03:01 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Hi, Ed, and welcome to the forums. I don't know if an IR thermometer is the best tool for measuring air temps. My understanding is that they work by sensing the radiation from solid objects. Maybe others will chime in and let us know if they are using them successfully for this purpose.


Ken
Reply With Quote
  #3  
Old 05-26-2010, 03:07 PM
thejoker thejoker is offline
Junior Member
 
Join Date: May 2010
Posts: 2
Default

Thanks Ken,

I think what you said makes sense. Hope to hear more inputs from the folks around the forum

Ed
Reply With Quote
  #4  
Old 07-28-2010, 10:44 PM
TheDude TheDude is offline
Junior Member
 
Join Date: Jul 2010
Posts: 6
Default

the real problem with ir thermometers is that the area the tool sees is directly proportionate to the distance to the object. for example if you are standing 20 feet away from where the red dot is, you're taking a picture of a 10' diameter area. the computer in the thermometer then comes to some average of the surface temps that it sees.

you would be much better off using a dry bulb thermometer or thermocouple(std temp probe for meters is a thermocouple)


OR...sbe sure to hold the unit a few inches from the surface ur trying to measure.

also ir thermometers tend to read differently depending on the material, copper pipe will read differently than brass or steel at the same temp. not sure why that is...


Enjoy!
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 09:29 AM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.