  #11  
Old 02-24-2006, 06:21 PM
gallant gallant is offline
Banned
 
Join Date: Oct 2005
Location: Atlanta
Posts: 57
Default

Nice product from APC. But it still has the same problems. How do I get chillwater to a new cooler unless I already have a chilled water system in place? I'm back to having "Bubba" in my data center with a torch.
Also, this unit doesn't have humidity control. Am I the only one who worries about static electricity?
What about condensate? Where does that go? Do I need drip pans under each unit?
And look carefully, I need a "CDU" (sold sperately) too.
And with this APC product I need to have my equipment in APC Infrastructure racks. No thanks, I'll stick to a 30ton liebert stlye CRAC blowing cold air.
Reply With Quote
  #12  
Old 04-11-2006, 10:07 PM
djbaik
Guest
 
Posts: n/a
Default Help !!!

Does anyone know or where to get this information ?

Typical data center cooling capacity ? in watts/sq.ft. etc. ?
Typical data center power density ? in watts/sq.ft. ?

Any study results showing the trend in cooling and power in data center ?

I am in a process of designing servers in 42U high cabinet that would go into "data center" but not too familiar with the physical constraints or power and cooling limitations.

Thanks !!!!!!
Reply With Quote
  #13  
Old 05-06-2006, 12:58 AM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Quote:
Does anyone know or where to get this information ?

Typical data center cooling capacity ? in watts/sq.ft. etc. ?
Typical data center power density ? in watts/sq.ft. ?

Any study results showing the trend in cooling and power in data center ?
Power = Cooling. There is no "typical" data center. For some excellent planning information, see whitepapers at http://www.upsite.com/TUIpages/tuihome.html.

.
Reply With Quote
  #14  
Old 05-10-2006, 01:00 AM
jhw539
Guest
 
Posts: n/a
Default

Quote:
Originally Posted by djbaik
Does anyone know or where to get this information ?

Typical data center cooling capacity ? in watts/sq.ft. etc. ?
Typical data center power density ? in watts/sq.ft. ?

Any study results showing the trend in cooling and power in data center ?

I am in a process of designing servers in 42U high cabinet that would go into "data center" but not too familiar with the physical constraints or power and cooling limitations.

Thanks !!!!!!
Datacenter loads vary enormously. Recent measurements of operating datacenters in CA found a range of 5 - 65 W/sf (see figure 5, pg 11 of this for a pretty graph). I have seen slightly higher, but eneral trends are useless for your equipment - it's going up now, who knows next year?.

Design values for cooling capacity are also all over the map - 100 - 150 w/sf are not uncommon, again entirely dependent on the equipment planned to be used and future growth assessments. Power density should equal the cooling capacity, but usually the design cooling capacity is quite a bit higher than the installed power density, and redundancy approaches usually result in a cooling capacity higher than the power density.

I do some mechanical design in datacenters and one thing I'd ask for from the server designers (is that you? is a very well defined heat exhaust. Hot aisle/cold aisle configurations are a very big deal for getting efficient and effective cooling in a high density enviroment (see the Uptime Institute white papers recommended above for great background info).
Reply With Quote
  #15  
Old 06-14-2006, 06:42 PM
Rmgill Rmgill is offline
Moderator
 
Join Date: Jun 2006
Location: Atlanta, Ga
Posts: 28
Default

I'm looking at the IBM Heat eXchanger doors right now for a Blade Server Deployment. Honestly, I'm pretty comfortable with the water in the data center (it's already running to each of my air handlers) and as I know the guys that have done our facilities work, I trust Cornbread (that's one of the contractors names, really!) and his skills with a torch when it comes to soldering up the copper pipes that feed the Coolant Distribution Unit.

Honestly, I'm more happy with the quality of work I get out of the same Contractors we've had working here at CNN for the past 10 years than I am with some of my co-workers that deploy systems into the Data Center. Given how the Electricians work with dangerous voltages and the HVAC guys work with dangerous voltages, heavy objects and flammable fuels, their capabilities and skills have less room for error. I still monitor their work, but if I'm around, I more or less trust them implicitly. I guess it does help that we've had the same contractors for the past 10 years.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 05:07 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.