Default Average rack configuration and power

We're building out a new DC and I have a couple of questions on what is average for a couple items.

1) Rack Configuration - What is the usual depth of a rack? My initial hunting seems to point at 36". What is acceptable row spacing? We are taking part of a building and are trying to get 4 rows in. Our footprint can adjust to accommodate, but we need to understand how far apart to space.

2) Rack Power - What is an average power feed into a rack? Since most modern computer/network equipment can run at 208VAC, I'm assuming we will be able to get away with mostly 208V to each rack. Which amperage do you guys default with for an average customer? 15? 30?

Thanks for your help.
Reply With Quote
  #2  
Old 11-17-2011, 08:38 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Because of the length of some newer tape libraries and rackmount servers, we have migrated from 42 in. to 48 in. deep racks. You should plan on 48 in. access for the front of the racks and 36 in. rear access. This gives racks an 11 ft. footprint. Maybe others can chime in on average rack power, but we have one facility using subfloor cooling that averages around 6 kW per rack and another using hot aisle containment that can accommodate 20 kW per rack.


Ken
__________________
DR/BC Planner

Last edited by KenB; 11-17-2011 at 08:45 PM.
Reply With Quote
  #3  
Old 11-17-2011, 10:06 PM
bline bline is offline
Junior Member
 
Join Date: Nov 2011
Posts: 3
Default

What about rack options besides depth? Square vs drilled, dead space for cables or PDU, etc.. Which options are required best compatibility? Any manufacturer suggestions?
Reply With Quote
  #4  
Old 11-18-2011, 12:02 AM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Not knowing any of your requirements, I'll say what works well for us. We use cabinets with built-in casters that are 42U high and 24 in. wide. The 24 in. width nicely accommodates our 19 in. wide servers and indexes well with our 24 in. raised floor panels. Higher than 42U racks bump into many overhead obstacles. We end up using the bottom few spaces for cable entry and UPS and the top of the rack for patch panels and rack switches, so we plan for a maximum of 75% rack fill.

We use racks with square hole rails, which accommodate most modern equipment mounting rails, and use cage nuts in case something needs to be mounted with screws. We try to limit rack weight to 2,000 lbs. to stay within the limits of the raised floor specs.

We prefer racks made by companies who do not manufacture servers and find APC's AR3300 racks to offer excellent value. Other very good brands recommended in other threads include Rittal, Emerson and Chatsworth.

Hope that helps.


Ken
__________________
DR/BC Planner

Last edited by KenB; 11-21-2011 at 01:05 AM.
Reply With Quote
  #5  
Old 11-21-2011, 12:01 AM
medialover medialover is offline
Junior Member
 
Join Date: Nov 2011
Posts: 11
Default

We have proceeded on a similar path Ken. We use Emerson racks and find they work very well for us. Some of our older servers fit more comfortably into these racks although I'm certain they would fit into other racks as well. We planned from the outset to limit each rack to less than 1,500 lbs. as we currently have lots of space for growth. The only thing we feel would limit the use of racks of the type we use would be some of the new rack cooling systems. Currently we use underfloor cooling and standard air-conditioning to keep our center cool.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 04:41 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.