Go Back   Data Center, Colocation, Cloud Computing, Storage, Dedicated Servers Forums > General DataCenter Discussion Forum > Data Center Design, Development, Building Systems and Operations

Reply

 

Thread Tools
  #1  
Old 02-22-2010, 10:25 PM
Zitibake Zitibake is offline
Senior Member
 
Join Date: Dec 2005
Posts: 113
Default genset capacity and datacenter standards

I have seen descriptions of the Tier-3 datacenters, as having power systems which are N+1, and sized to support "90% N" (versus 100% of "N" for Tier-2).

Does anyone know how to translate that for use with "failover" designs? For example, where one "catcher" UPS provides power to the bypass input of the primary UPS; or where there are cascading transfer switches, and a "swing" genset backs-up the primary genset?

I would guess that you still wouldn't exceed 90% of one UPS. But for the generator, would you want to stay below 90% of Standby load, Prime load, or Continuous load rating? Also, it seems like generators should be sized to handle the maximum load with allowable voltage drop, rather than some percentage of a rating; but I haven't seen this mentioned in datacenter tiers, or in TIA-942.
Reply With Quote
  #2  
Old 02-23-2010, 03:46 AM
Zitibake Zitibake is offline
Senior Member
 
Join Date: Dec 2005
Posts: 113
Default

I found a relevant recommendation:

"Engine generators for Tier III and IV sites" (my situation) "shall not have a limitation on consecutive hours of operation when loaded to 'N' demand."

I note that it doesn't say "loaded to 90% of 'N'". So I'd interpret this to mean that the Continuous, or de-rated Prime rating of the genset, must be greater than total load.

I'll still say that THD or motor load could make this recommendation a moot point.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 10:02 AM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.