Default HVAC Design

We recently built a small data center where I work. It has two rows of three racks each, back to back, so as to create a hot aisle between the two rows of servers (at the back of all the racks).

We had spec'd it to have two return air vents over the top of the hot aisle, and then have the cool air being blown in via registers all around the room. However, the HVAC guys thought we were crazy, so they put one large return air vent on the wall (closest to where the outside HVAC unit is) and put a few cold air registers over the server racks.

What seems to be happening is the cold air is simply being blown into the room and sucked out, without proper cooling of the server racks. We are struggling to keep the room cool.

Should we go back to our original plan, which was to have cold air vents circling the room, and the return vents over the top of the hot aisle between the server racks. The theory was this would suck the air 'across' and through the servers', and then the return air vents would im################y pull hot air out of the room.

Thanks in advance for any advice.
Reply With Quote
  #2  
Old 05-10-2009, 05:44 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Your best bet is to engage an engineer familiar with data center cooling. There are a lot of variables to balance. It sounds like your original design has promise, but the contractor didn't build it right. I'd recommend getting a design that is verified to work on paper before asking the contractor to rework the job.


Ken
Reply With Quote
  #3  
Old 05-10-2009, 07:59 PM
cherokeeflyer cherokeeflyer is offline
Junior Member
 
Join Date: May 2009
Posts: 14
Default

In the area that I live, there is no one familiar with DC construction, so we have a tendency to rely heavily on internet research. I think we had come up with something that would work, but the local HVAC guys ignored it and put in venting that they would do for a normal room.

I might try and find an engineer I can work with long distance to see about the redesign.
Reply With Quote
  #4  
Old 05-10-2009, 08:42 PM
dcrelocation dcrelocation is offline
Member
 
Join Date: Feb 2008
Posts: 38
Default

As stated before you need to contact someone that work with you specifically looking at your hot air return,your cooling and try and eliminate any commingling of the cold and hot air to name a few.
Reply With Quote
  #5  
Old 05-10-2009, 10:08 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Quote:
Originally Posted by cherokeeflyer View Post
In the area that I live, there is no one familiar with DC construction, so we have a tendency to rely heavily on internet research.
Your profile doesn't say. Where are you located?


Ken
Reply With Quote
  #6  
Old 05-11-2009, 01:16 AM
cherokeeflyer cherokeeflyer is offline
Junior Member
 
Join Date: May 2009
Posts: 14
Default

Quote:
Originally Posted by KenB View Post
Your profile doesn't say. Where are you located?


Ken
Arkansas. A couple hours from Memphis and a couple hours from Little Rock.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 01:01 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.