Default Tier 4

Anyone know if a data center with a single utility feed and a single generator i considered tier 4?
Reply With Quote
  #2  
Old 11-06-2009, 01:45 AM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Nope. G.5 says "The building should have at least two utility feeders from different utility substations for redundancy."


Ken
Reply With Quote
  #3  
Old 11-08-2009, 10:47 PM
raid raid is offline
Member
 
Join Date: Aug 2005
Posts: 69
Default

Quote:
Originally Posted by KenB View Post
Nope. G.5 says "The building should have at least two utility feeders from different utility substations for redundancy."
Ken

Have often wondered what is meant by redundant utility feeds. If you have two substation transformers on site (they could even be in the same room) and they both go back to the same transformer upstream, is this any improvement? How far upstream do you have to go to get the redundancy level required to meet Tier 4?
Reply With Quote
  #4  
Old 11-09-2009, 07:30 AM
smilers smilers is offline
Junior Member
 
Join Date: Jul 2009
Posts: 10
Default

Quote:
Originally Posted by Neoeclectic View Post
Anyone know if a data center with a single utility feed and a single generator i considered tier 4?
Technically, No. But in countries where there is only one universal utility company(by government). There isn't a choice. Instead, improvising (i.e. N+2 or 2N+2) would be ideally close to Tier 4.
Reply With Quote
  #5  
Old 11-09-2009, 10:18 PM
Neoeclectic Neoeclectic is offline
Member
 
Join Date: Oct 2008
Posts: 85
Default

Thanks. I was able to sort of figure it out over the weekend. I think technically our facility is (N+1) being 1 utility feed and 1 generator. TIA says that 2(N+1) would be more inline with T4. My interpretation of that is two unique utility feeds and a generator each.

Does that sound about right?
Reply With Quote
  #6  
Old 11-09-2009, 11:00 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Quote:
Originally Posted by raid View Post
Ken

Have often wondered what is meant by redundant utility feeds. If you have two substation transformers on site (they could even be in the same room) and they both go back to the same transformer upstream, is this any improvement? How far upstream do you have to go to get the redundancy level required to meet Tier 4?
Good point. Transformers and other redundant gear should probably have some "geographic diversity," so that important eggs don't share the same basket.


Ken
Reply With Quote
  #7  
Old 12-16-2009, 10:56 PM
SteelVault SteelVault is offline
Junior Member
 
Join Date: Dec 2009
Posts: 5
Default

Quote:
Originally Posted by Neoeclectic View Post
Thanks. I was able to sort of figure it out over the weekend. I think technically our facility is (N+1) being 1 utility feed and 1 generator. TIA says that 2(N+1) would be more inline with T4. My interpretation of that is two unique utility feeds and a generator each.

Does that sound about right?
That is the exact definition. Also look at: http://www.adc.com/Library/Literature/102264AE.pdf
or Data center - Wikipedia, the free encyclopedia

good luck
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 11:13 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.