Default UPS v Standby Generator - DR Site

Hi there. I'm after some advice please, if anyone can help. I'm in the UK by the way.

We have a small (but business important) data centre with 6 racks of servers in it.

I'm looking to price up relocating this, and as part of this exercise, have been presented two options to consider on emergency power;

a) Having a UPS that runs for about 30 minutes maximum, with a standby generator on-site, designed and fulled for several days running (i.e. UPS just runs long enough to get generator up) or

b) A UPS than can run for 24 hours, with a 24 hour call off contract on a plug-in generator. (removes the need for an on-site generator)

What are peoples views on the relative costs of each option please, and also whether there are any other key factors that significantly make one option beter than the other ?

Thanks for any advice
Ian
Reply With Quote
  #2  
Old 05-10-2011, 03:21 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Think of all the plausible reasons your generator delivery guy might not be able to make it to your site before your batteries run out and put a price on those scenarios. Don't forget to price out the purchase and replacement costs of batteries needed to run your power and cooling for 24 hours. With just-in-time generator delivery, you'll need the infrastructure (transfer switch, alternate electrical feeders, parking spot) for a generator, anyway, so your savings will only be generator purchase and maintenance costs. I think a small generator of your own will turn out to be cheap insurance.

Also, 30 minutes is too long for automatic transfer to a standby generator; 5-10 minutes should be plenty.

Just my opinion.


Ken
Reply With Quote
  #3  
Old 05-11-2011, 03:39 PM
mistapike mistapike is offline
Junior Member
 
Join Date: May 2011
Posts: 2
Default

Thanks Ken - your thoughts are very helpful. I am inclined to agree with you -(my management want me to present both options to them)
Reply With Quote
  #4  
Old 06-02-2011, 01:00 AM
raid raid is offline
Member
 
Join Date: Aug 2005
Posts: 69
Default

It’s always a good idea to present management with at least 3 options, that way they think they are making a decision. This is called the goldilocks approach, one is too big, one is too small and one is just right. You just have to ensure that the options you don’t want them to select are either too expensive or place the business at an unacceptable risk.
Reply With Quote
  #5  
Old 06-23-2011, 10:00 AM
_JT_ _JT_ is offline
Junior Member
 
Join Date: Jan 2010
Posts: 6
Default

Definitely recommending 5-10 min UPS in combination with on-site generators. Even with the best UPS systems despite best battery monitoring systems you actually never know how long the batteries are going to last...plus all the concerns that Ken was mentioning.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 10:13 AM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.