How many 1U servers can be put in 42U, I dont think so we can packaged 42 1U, there will be heating issue. How many do you people mosly fit into 42U cabinets.
How many 1U servers can be put in 42U, I dont think so we can packaged 42 1U, there will be heating issue. How many do you people mosly fit into 42U cabinets.
Heating is an issue, but also power consumption and how much of both you may use as result of the TOS of your contract. Generally speaking airconditioning and power feed allows to use 600Watt per square meter. Sometimes that is a praktical limit (the airco and/or UPS can't take anymore as an average), sometimes it is a financial limit (you have to pay more to use more).
I have seen 55U cabinets packed with 1U servercases (at least 40), but that is really exceptional. It takes a very 'cool' space and good servers.
It also depends on the DC configuration. You can slap cabinets full if the AC is ducted into the bottom of the cabinet. A little less if they are using mesh doors and are ducting under the raised floor right to the front of the cabinet, and a lot less if your not in a raised floor environment.
As for costs, the colo provider is going to factor AC into the cost of providing power. That's why you typically see prices charged per breakered AMP, and when you do the math based upon what power costs, you see that it tends to have quite a bit of markup to it (AC Costs+Markup).
To determine what size AC Unit you require to keep your server room cool you have to determine how much power your equipment is using. The following is a good estimate based on a basic configuration of your equipment.
Use the following conversion factor when sizing your AC Unit.
1000W = 0.284 Tons
1 Ton = 3517W
You will need at least 0.5 Tons just for your equipment, this does not include everything else in the room. Typically a small commercial grade AC unit will be 1.5 Tons which would be sufficient for a small server room with your given equipment.
I would speak with the General Contractor or whoever is selling you the AC unit for their professional opinion. A good GC will use a clamp meter to determine the exact power consumption of your equipment. Some GCs will go as far as using a Thermal Imaging device to make sure there are no hot spots in your datacenter.
If you have any questions please don't hesitate to contact me or any of the technical support staff at www.RackSolutions.com
Our datacenter is set up with raised floor, down draft AC and has plenty of power available. Due to this, we are able to routinely get 36-38 1U boxes in a rack, as long as we stick with servers that have a soundly engineered cooling solution. We leave 1U for our switch, and we typically use 2-3 shelves per rack which take up 0.5U each. The rest is all servers.
It is also important to take your time and do a good job routing cables and doing a nice clean install - the better job you do with that, the better your airflow, which will in turn allow you to maximize your rack space.
I have some pics of our installs, let me know if you would like to see how we do it.
Everyone is making the assumption that you have a 40A/110V connection to your cabinet (which is the exception, not the rule). Most cabinets are 20A/110V or 15A/110V in which case you can forget about putting more than 20 - 25 systems.