Default how to calculate cooling needs of DC

Hello,
Is there a thumb rule to follow to determine how much cooling is required for a data center? is it calculated on the basis of cooling per server?
Reply With Quote
  #2  
Old 02-17-2012, 03:19 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Two rules of thumb I use:
  • Power in = heat out (3412 BTU/kW)
  • Airflow required is 150 cfm/kW
I'd like to know what other "guesstimates" people use, too.

For a more formal calculation, you may be interested in the following white paper from APC: Calculating Total Cooling Requirements for Data Centers

Ken
__________________
DR/BC Planner
Reply With Quote
  #3  
Old 02-28-2012, 01:09 PM
bell bell is offline
Member
 
Join Date: Dec 2011
Posts: 77
Default

calculating on the basis of cooling per server is not feasible. the heat dissipated when a server is on full swing and when it is free is different. you will have to monitor the usage and then adjust the cooling. problems will arise even if its overcooled. but i would like to know how it is actually measured in different data centers
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 12:57 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.