Default Action on the event of Fire Detection?

I would like to understand if there is a best practice in the operation of Fire Suppression and associated controls within a small Data Centre - 50 racks.

The Data Centre concerned recently experienced an activation of the FM200 based Fire Suppression. The cause is believed to been a fault however it has raised question as to the correct operation.

On activation of the Fire Detection, Power to the UPS, Servers and Storage etc was cut. However the Air Conditioning remained running.

This seemed odd to me. If the servers were off, there was little need for the air conditioning, and if power needs to be cut, it should be to all electrical systems.

Could someone advise - what the common approach would normally be?
For clean systems such as FM200 is it common practice to leave equipment running, which has the benefit of preserving service, but at the risk that the fire (if there is one) may not be extinguished.

It is probably worth mentioning that the Data Centre concerned houses the UPS in the same sealed environment as the Servers etc, so from a Fire Risk perspective, I would assume this presents the biggest potential risk.

Thanks
Reply With Quote
  #2  
Old 05-25-2016, 11:16 AM
adilkhan009 adilkhan009 is offline
Senior Member
 
Join Date: Feb 2016
Location: Mumbai
Posts: 1,084
Default

Very helpful and good post.
Reply With Quote
  #3  
Old 06-07-2016, 12:51 PM
adilkhan009 adilkhan009 is offline
Senior Member
 
Join Date: Feb 2016
Location: Mumbai
Posts: 1,084
Default

Organizations spend a lot of money protecting data centers from the risk of downtime. And those investments — whether in uninterruptible power supply (UPS) systems, powerful air conditioning systems or emergency generators — are justified by the greater costs the organization would bear if the data center were to go down. But the risk of fire also deserves careful attention from facility manager.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 06:19 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.