Default power normalizing question

When we run production serves and when the power goes down UPS will kicked in, after that when would you normalize? Is there a rule? Or Just we can switch it back to the PDU?
Reply With Quote
  #2  
Old 07-04-2009, 08:25 AM
raid raid is offline
Member
 
Join Date: Aug 2005
Posts: 69
Default

I think the question is about when you use a UPS in line interactive mode (power is normally sourced via the STS). When the supply goes out of tolerance, the STS will kick in to run the load from the UPS. So when do you decide to switch it back, is it auto or manual.

This is how I read the question.

If line interactive is fine for you, make it automatic after the supply stays within tolerance for 15 minutes.