Default datacenter cabling service

Guys,

When you run cable under the floor, does it generate lots of magnetic field and would that affect switches?
Reply With Quote
  #2  
Old 09-30-2008, 06:21 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

Unshielded data cables can pick up electrical noise from a variety of sources, which certainly could affect switch performance.

Ken
Reply With Quote
  #3  
Old 10-01-2008, 03:20 PM
whcdavid's Avatar
whcdavid whcdavid is offline
Administrator
 
Join Date: Mar 2004
Posts: 901
Default

Ken,

Do you see a big defference in performance? Or just little bit of performance.
__________________
WebHostingChat ( Web Hosting Forum)
DatacenterSearch (Find your Datacenter)
YOU FAIL ONLY WHEN YOU FAIL TO TRY
Reply With Quote
  #4  
Old 10-01-2008, 07:12 PM
KenB's Avatar
KenB KenB is offline
Administrator
 
Join Date: Jan 2006
Location: Pittsburgh, PA
Posts: 468
Default

I have seen only small performance hits, but depending on the source of noise, the effect could be huge. Electrical cables, transformers, motors, power supplies and many types of electronic equipment can cause interference. Indicated by a high bit-error rate (BER), the problem can sometimes be solved by re-routing the cable(s). Otherwise, metal raceway or shielded cable are possible solutions.

Ken

Last edited by KenB; 10-01-2008 at 07:42 PM.
Reply With Quote
  #5  
Old 10-13-2008, 04:37 PM
cogbuddy cogbuddy is offline
Junior Member
 
Join Date: Oct 2008
Posts: 26
Default

Yes there would be some interruptions and it may cause some effect. This cannot be avoided. how ever it may have been shielded, still the effect can be a minimum only. The magnetic effect would not be there but we can feel some electrical disturbances and fluctuations.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 11:32 PM.

Member Area



Data Center Industry Daily News


Cloud and Dedicated Hosting


Sponsors Managed Servers Sponsored by DedicatedNOW.
Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.