Default Emerson-Liebert UPS 150 kVA

(2) 300 kVA redundant w/ static switch and maintenance bypass system (batteries not included)

The modules are 150kVA / 120kW 480V in and out space savers.

The system control cabinet the USCCT is 100% rated for 560 amperes. The output of each 150kVA module @ 480V is 180 amperes. That means the two modules could run either 150kVA redundant or 300kVA for capacity.

Given the ampere rating of the system control cabinet, a third module can be added to give you 300kVA redundant or 450kVA capacity. A fourth module can be added but only for redundancy, the system would then be 450kVA redundant.

There are only two battery cabinets, one for each module. Run time at full load with new batteries would be 9 minutes.

Let me know if anyone is interested.

FOB NJ