Default

bline
There is nothing wrong with this method of design in theory and if you were to gain access to many of the fresh air cooled data centres around the world you would see this design in action. Although many of these designs use the complete room side walls to deliver the air into the room so that the airspeed is reduced and pressure is correct.

There is a number of things to be aware of when distributing your air in this fashion.
Firstly the air will be entering the room at very high speeds especially if you have a large room which requires large amounts of air volume.
Here are some suggestions to overcome this problem.
1 Firstly position the CRAC units perpendicular to the rows.
2 It may be possible to reduce the velocity of the air by positioning the CRAC;s so that it is opposite the HOT aisles. This will mean it has to hit the containment doors first and then go around the corner into the cold aisle.
3 You will also need a good gap between the CRAC units and the start of the rows. (At least three tiles)
4 You will need wide cold aisles.

One other factor to consider is what happens during CRAC failure especially failure of the the end units, ie the last CRAC in the row. There is a high possability of creating a hot spot.
NOTE all CRAC units will need to be maintained at regular intervals so this condition will arrise at least twice a year.


I have worked on data centre layouts for many years and always used our inhouse CFD to proof the airflow patterns and this is definitely one design concept that will have to be modelled.

But In theory it can be worked.

Vincent