That 80% is mandated in the USA by the National Electrical Code. For continuous use (3 hours or more, i.e. servers that are always on inside a data center), circuit breakers are rated at 80% of their nominal capacity. It's okay to go above 80% use, but it's not okay to stay there.
__________________