bell 03-13-2012 06:02 PM

CRAH and CRAC
 
what is the difference between CRAH and CRAC?

KenB 03-13-2012 07:30 PM

An air conditioner has its own mechanism for cooling, while an air handler does not.

Ken

sweetgreen 03-16-2012 01:36 PM

are CRAC and CRAH even used these days? or has the airflow management system completely obliterated CRACs and CRAHs?

KenB 03-16-2012 03:37 PM

b2netsolutions: That's the only difference.

sweetgreen: I think it's accurate to say that CRAHs and CRACs are still key components of airflow management systems.


Ken

vincent_byrne 03-16-2012 05:17 PM

Bell
A CRAC and CRAH carry out the exact same function and still cool 90% of all data centres globally.
The difference between the two is simple. A CRAC unit is cooled by refrigerant and a CRAH is cooled by water. CRAC units usually have a single outside condensor for each CRAC unit where as a CRAH unit will get its chilled water form a chilleed water circuit from a bank of chillers.
Generally we see CRAC units in smaller data centres or in data centre in locations with extremely high temperatures. But even refrigerants have their maximum operating temperatures for examplle R22 can operate up to about 46degC but as I have experienced in some of the middle east this is sometimes not enough as some locations go up to 52degC. Not a nice location to have to work

So yes they still do play a major role in the provision of cooling in the data centre. For data centres with raised floors thses types of units deliver the cold air into the floor void.

Vincent

jackton 03-19-2012 09:45 AM

sweetgreen, even if u use airflow management techniques, you have to use something to cool the directed heated air, don't you? that's what CRACs do. the heated air is directed from hot aisles to CRACs for cooling